Solax X3-7.0-T-D RS485 readout possible? #1224
-
I've been struggling with getting a RS485 readout from my Solax X3-7.0-T-D inverter (with pocketlan 2.0). The manual is in line with what's shown in this tread, with RS485 UTP connection on pin 4 and 5. I've now tried with WaveShare USB and ethernet RS485 converters, but both give a connection time-out error when testing via modpoll. I received a modbus protocol from Solax support for this inverter type, but fail to get a readout whatsoever. Does anybody have any experience with this type? Note that there is no RS485 specific setting in any of the inverter menus. It does have 'export control' enable / disable, but I think this only applies when connecting an actual three-phase current meter. |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 4 replies
-
What Baud rate are you trying to use? Is this a Gen4 Hybrid? If so it's 19,200 you can see a list of the common ones here |
Beta Was this translation helpful? Give feedback.
-
Solved it! Following the comment of @wills106 I ignored the Solax manuals suggestion to use address 11. Finally got a reading from the WaveShare ETH module using modpoll tool. For example, to get today's output: Now to get it working with your HA extension... |
Beta Was this translation helpful? Give feedback.
Solved it!
Following the comment of @wills106 I ignored the Solax manuals suggestion to use address 11. Finally got a reading from the WaveShare ETH module using modpoll tool. For example, to get today's output:
modpoll -1 -a 1 -r 0x426 -c 1 -t 3 -o 1 -l 100 -m tcp [WaveShare IP]
. Important to get the settings of the WaveShare exactly like in the screenshots below:In "more advanced settings":
Now to get it working with your HA extension...